Dear all,
I am using the ROSCO controller to simulate a floating wind turbine. According to the above discussions, I downloaded the controller files DISCON_IEA_offshore, IEA-10.0-198-RWT_DISCON.IN and IEA-10.0-198-RWT_Cp_Ct_Cq.txt, applied them in the ServoDyn file and ran the simulation.
The question is that no matter I enable or disable the pitch control, the blade pitch angle came to be 90 after several seconds, and the power coefficient cp droped to about -1. Also, the power exceeds the rated power (10 MW), reaches to about 350MW, which is quite strange. I guess the power issue is related to the blade pitch error, but I cannot figure out what’s wrong with my input files. I also tried to change the wind speed or disable the inflow wind, but the problem was not solved.
The related results and the ServoDyn file is shown below. I would be appreciate if anyone could help to check and give any suggestions on this problem.
------- SERVODYN v1.05.* INPUT FILE --------------------------------------------
Generated with AeroElasticSE FAST driver
---------------------- SIMULATION CONTROL --------------------------------------
False Echo - Echo input data to .ech (flag)
“default” DT - Communication interval for controllers (s) (or “default”)
---------------------- PITCH CONTROL -------------------------------------------
5 PCMode - Pitch control mode {0: none, 3: user-defined from routine PitchCntrl, 4: user-defined from Simulink/Labview, 5: user-defined from Bladed-style DLL} (switch)
0.0 TPCOn - Time to enable active pitch control (s) [unused when PCMode=0]
9999.9 TPitManS(1) - Time to start override pitch maneuver for blade 1 and end standard pitch control (s)
9999.9 TPitManS(2) - Time to start override pitch maneuver for blade 2 and end standard pitch control (s)
9999.9 TPitManS(3) - Time to start override pitch maneuver for blade 3 and end standard pitch control (s) [unused for 2 blades]
10.0 PitManRat(1) - Pitch rate at which override pitch maneuver heads toward final pitch angle for blade 1 (deg/s)
10.0 PitManRat(2) - Pitch rate at which override pitch maneuver heads toward final pitch angle for blade 2 (deg/s)
10.0 PitManRat(3) - Pitch rate at which override pitch maneuver heads toward final pitch angle for blade 3 (deg/s) [unused for 2 blades]
0.0 BlPitchF(1) - Blade 1 final pitch for pitch maneuvers (degrees)
0.0 BlPitchF(2) - Blade 2 final pitch for pitch maneuvers (degrees)
0.0 BlPitchF(3) - Blade 3 final pitch for pitch maneuvers (degrees) [unused for 2 blades]
---------------------- GENERATOR AND TORQUE CONTROL ----------------------------
5 VSContrl - Variable-speed control mode {0: none, 1: simple VS, 3: user-defined from routine UserVSCont, 4: user-defined from Simulink/Labview, 5: user-defined from Bladed-style DLL} (switch)
1 GenModel - Generator model {1: simple, 2: Thevenin, 3: user-defined from routine UserGen} (switch) [used only when VSContrl=0]
94.0 GenEff - Generator efficiency [ignored by the Thevenin and user-defined generator models] (%)
True GenTiStr - Method to start the generator {T: timed using TimGenOn, F: generator speed using SpdGenOn} (flag)
True GenTiStp - Method to stop the generator {T: timed using TimGenOf, F: when generator power = 0} (flag)
9999.9 SpdGenOn - Generator speed to turn on the generator for a startup (HSS speed) (rpm) [used only when GenTiStr=False]
0.0 TimGenOn - Time to turn on the generator for a startup (s) [used only when GenTiStr=True]
9999.9 TimGenOf - Time to turn off the generator (s) [used only when GenTiStp=True]
---------------------- SIMPLE VARIABLE-SPEED TORQUE CONTROL --------------------
49.76235 VS_RtGnSp - Rated generator speed for simple variable-speed generator control (HSS side) (rpm) [used only when VSContrl=1]
200955.1398 VS_RtTq - Rated generator torque/constant generator torque in Region 3 for simple variable-speed generator control (HSS side) (N-m) [used only when VSContrl=1]
81.1516502 VS_Rgn2K - Generator torque constant in Region 2 for simple variable-speed generator control (HSS side) (N-m/rpm^2) [used only when VSContrl=1]
9.9999e-06 VS_SlPc - Rated generator slip percentage in Region 2 1/2 for simple variable-speed generator control (%) [used only when VSContrl=1]
---------------------- SIMPLE INDUCTION GENERATOR ------------------------------
9999.9 SIG_SlPc - Rated generator slip percentage (%) [used only when VSContrl=0 and GenModel=1]
9999.9 SIG_SySp - Synchronous (zero-torque) generator speed (rpm) [used only when VSContrl=0 and GenModel=1]
9999.9 SIG_RtTq - Rated torque (N-m) [used only when VSContrl=0 and GenModel=1]
9999.9 SIG_PORt - Pull-out ratio (Tpullout/Trated) (-) [used only when VSContrl=0 and GenModel=1]
---------------------- THEVENIN-EQUIVALENT INDUCTION GENERATOR -----------------
9999.9 TEC_Freq - Line frequency [50 or 60] (Hz) [used only when VSContrl=0 and GenModel=2]
9998 TEC_NPol - Number of poles [even integer > 0] (-) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_SRes - Stator resistance (ohms) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_RRes - Rotor resistance (ohms) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_VLL - Line-to-line RMS voltage (volts) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_SLR - Stator leakage reactance (ohms) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_RLR - Rotor leakage reactance (ohms) [used only when VSContrl=0 and GenModel=2]
9999.9 TEC_MR - Magnetizing reactance (ohms) [used only when VSContrl=0 and GenModel=2]
---------------------- HIGH-SPEED SHAFT BRAKE ----------------------------------
0 HSSBrMode - HSS brake model {0: none, 1: simple, 3: user-defined from routine UserHSSBr, 4: user-defined from Simulink/Labview, 5: user-defined from Bladed-style DLL} (switch)
9999.9 THSSBrDp - Time to initiate deployment of the HSS brake (s)
0.6 HSSBrDT - Time for HSS-brake to reach full deployment once initiated (sec) [used only when HSSBrMode=1]
28116.2 HSSBrTqF - Fully deployed HSS-brake torque (N-m)
---------------------- NACELLE-YAW CONTROL -------------------------------------
0 YCMode - Yaw control mode {0: none, 3: user-defined from routine UserYawCont, 4: user-defined from Simulink/Labview, 5: user-defined from Bladed-style DLL} (switch)
9999.9 TYCOn - Time to enable active yaw control (s) [unused when YCMode=0]
0.0 YawNeut - Neutral yaw position–yaw spring force is zero at this yaw (degrees)
9028320000.0 YawSpr - Nacelle-yaw spring constant (N-m/rad)
19160000.0 YawDamp - Nacelle-yaw damping constant (N-m/(rad/s))
9999.9 TYawManS - Time to start override yaw maneuver and end standard yaw control (s)
0.25 YawManRat - Yaw maneuver rate (in absolute value) (deg/s)
0.0 NacYawF - Final yaw angle for override yaw maneuvers (degrees)
---------------------- TUNED MASS DAMPER ---------------------------------------
False CompNTMD - Compute nacelle tuned mass damper {true/false} (flag)
“” NTMDfile - Name of the file for nacelle tuned mass damper (quoted string) [unused when CompNTMD is false]
False CompTTMD - Compute tower tuned mass damper {true/false} (flag)
“” TTMDfile - Name of the file for tower tuned mass damper (quoted string) [unused when CompTTMD is false]
---------------------- BLADED INTERFACE ---------------------------------------- [used only with Bladed Interface]
“D:\OpenFAST\DTU_10MW\DISCON_IEA_offshore.dll” DLL_FileName - Name/location of the dynamic library {.dll [Windows] or .so [Linux]} in the Bladed-DLL format (-) [used only with Bladed Interface]
“D:\OpenFAST\DTU_10MW\IEA-10.0-198-RWT_DISCON.IN” DLL_InFile - Name of input file sent to the DLL (-) [used only with Bladed Interface]
“DISCON” DLL_ProcName - Name of procedure in DLL to be called (-) [case sensitive; used only with DLL Interface]
“default” DLL_DT - Communication interval for dynamic library (s) (or “default”) [used only with Bladed Interface]
False DLL_Ramp - Whether a linear ramp should be used between DLL_DT time steps [introduces time shift when true] (flag) [used only with Bladed Interface]
9999.9 BPCutoff - Cuttoff frequency for low-pass filter on blade pitch from DLL (Hz) [used only with Bladed Interface]
0.0 NacYaw_North - Reference yaw angle of the nacelle when the upwind end points due North (deg) [used only with Bladed Interface]
0 Ptch_Cntrl - Record 28: Use individual pitch control {0: collective pitch; 1: individual pitch control} (switch) [used only with Bladed Interface]
0.0 Ptch_SetPnt - Record 5: Below-rated pitch angle set-point (deg) [used only with Bladed Interface]
0.0 Ptch_Min - Record 6: Minimum pitch angle (deg) [used only with Bladed Interface]
0.0 Ptch_Max - Record 7: Maximum pitch angle (deg) [used only with Bladed Interface]
0.0 PtchRate_Min - Record 8: Minimum pitch rate (most negative value allowed) (deg/s) [used only with Bladed Interface]
0.0 PtchRate_Max - Record 9: Maximum pitch rate (deg/s) [used only with Bladed Interface]
0.0 Gain_OM - Record 16: Optimal mode gain (Nm/(rad/s)^2) [used only with Bladed Interface]
0.0 GenSpd_MinOM - Record 17: Minimum generator speed (rpm) [used only with Bladed Interface]
0.0 GenSpd_MaxOM - Record 18: Optimal mode maximum speed (rpm) [used only with Bladed Interface]
0.0 GenSpd_Dem - Record 19: Demanded generator speed above rated (rpm) [used only with Bladed Interface]
0.0 GenTrq_Dem - Record 22: Demanded generator torque above rated (Nm) [used only with Bladed Interface]
0.0 GenPwr_Dem - Record 13: Demanded power (W) [used only with Bladed Interface]
---------------------- BLADED INTERFACE TORQUE-SPEED LOOK-UP TABLE -------------
0 DLL_NumTrq - Record 26: No. of points in torque-speed look-up table {0 = none and use the optimal mode parameters; nonzero = ignore the optimal mode PARAMETERs by setting Record 16 to 0.0} (-) [used only with Bladed Interface]
GenSpd_TLU GenTrq_TLU
(rpm) (Nm)
---------------------- OUTPUT --------------------------------------------------
True SumPrint - Print summary data to .sum (flag) (currently unused)
1 OutFile - Switch to determine where output will be placed: {1: in module output file only; 2: in glue code output file only; 3: both} (currently unused)
True TabDelim - Use tab delimiters in text tabular output file? (flag) (currently unused)
“ES10.3E2” OutFmt - Format used for text tabular output (except time). Resulting field should be 10 characters. (quoted string) (currently unused)
0.0 TStart - Time to begin tabular output (s) (currently unused)
OutList - The next line(s) contains a list of output parameters. See OutListParameters.xlsx for a listing of available output channels, (-)
“GenPwr”
“GenTq”
END of input file (the word “END” must appear in the first 3 columns of this last OutList line)
Regards,
Yajun